Hello,
We have 1756-OF6CI module on Controllogix chassis controlling an actuator by applying 4-20 mA. The actuator is for opening and closing a valve. The 4mA is for Close command and 20mA is for Open.
The problem we face is at PLC power up.If the valve is in open position and a power off occur and PLC shutdown then when power come back the 1756-OF6CI at power up send close command to the actuator and the valve start to close during first 15 seconds and it goes toward close about 20% and after that it start to open again. All this happens during power up automatically without close command being issued from the HMI.
Is there any way to avoid that at power up and keep the valve at open position.
Thanks
We have 1756-OF6CI module on Controllogix chassis controlling an actuator by applying 4-20 mA. The actuator is for opening and closing a valve. The 4mA is for Close command and 20mA is for Open.
The problem we face is at PLC power up.If the valve is in open position and a power off occur and PLC shutdown then when power come back the 1756-OF6CI at power up send close command to the actuator and the valve start to close during first 15 seconds and it goes toward close about 20% and after that it start to open again. All this happens during power up automatically without close command being issued from the HMI.