A couple of days ago 1768-l45/b CPU from a machine stopped due to an error.
PWR-Green, Ok-RED, I/O PWR-RED
So I removed all the other I/O Module and connect the CPU with power supply. But the same error occurred there too.
I tried to communicate the CPU using RSlinx. But It can't find the CPU. So I am unable to reset it. and the front button isn't working either.
Is there anything I can do to recover it?
Here is a picture of the CPU.
https://ibb.co/5MBpHj5
5MBpHj5
If the OK indicator is solid Red, (not blinking), then the controller detected a Non-recoverable Major Fault, and in that circumstance it clears the project from its memory.
This is strengthened by the fact that the I/O LED is OFF, which either means that there are no I/O modules in the project configuration (unlikely), or there is no project in the controller.
If cycling power and re-downloading the project does not clear the fault, then it is possible that the controller has died, but you will need to get online....
Have you tried communication with RSLinx on the serial port? The correct cable is a 17xx-CP3, virtually any -CP3 cable will work. Full procedure for getting online to the controller here, pages 23 and onward... Auto-configure usually works every time....
I am currently running revision 17.1 on a L45 series B AB processor to control a SEW PLC with 2 SEW inverters. There is no issues communicating...
3,380
Wizards, I have this older machine, running v20.19. We have a huge lag when trying to go online with this bad boy. This is one of my oldest...
1,674
Hi, Is it possible to write tag using MSG in two diffirent controllers in separated networks using Dual-IP? I need to do something like that: 1...
1,602
Hey all. Perhaps a distributor question but some opinion never hurt. I use a ton of L43 and L45 processors. Many already installed and still...
2,179
Hello, I have been asked to change controller from 1768-L45 to 1769-L36ERS, as 1768-L45 is getting absolute. I have attached IO configuration...
2,006