1769-HSC Configuration Error
bwolten
Mar 2014
Sumas Washington
Flashing Red OK Status indicator :
Rockwell Automation Publication 1769-UM006E-EN-P - July 2013
Table 23 - Configuration Error Codes pg 117
These types of module errors are typically reported in the controllerÂ’s I/O status file. Refer to
your controller manual for details.
if module has a Flashing Red OK Status indicator, where can i view the error codes described in Table 23 using RSLogix 500???
The 1769-HSC is a compactlogix module, you will need RSLogix 5000 to view status information.
I would assume error information can be found in the input tag; if the module is located in the local chassis this would be Local:[Module#]:I.Fault
the 1769-HSC can be used on a 1500
I don't think the codes are readily available from using RS500, unfortunately. You may have to look at the data arrays to identify the error flags. The locations of those flags may help point in you the right direction
Thanks for the correction; so used to working with compactlogix I'd forgotten that 1769 modules can be used with micro as well.
Odd that in a compactlogix the fault word is part of the input tag but apparently isn't actually part of the input array that's accessible in 500.
@bwolten Was this a previously running system that has now faulted?
Table 31 shows the input array which contains some error flags, as BlueAltezza mentions the input data file is probably the place to start.
Does Anyone know what we should be configuring a hand pulse generator on a 1769-HSC card.I would really like to know.
2,274
Hello: I use the 1769-HSC module in the compactlogix system, the cpu1769-L32E, now I use the 1769-hsc output, but i can't configuration and...
1,694
Hi all, Before I ask my question, a list of hardware may assist in the search for a solution. Micrologix 1500 Base Unit: 1764-24BWA Ser B...
11,888
Hello all. I am having trouble setting up my HSC to count pulses from a prox switch. I have it wired to the prox and I see the .InputStateA0...
1,373
Here is my hail Mary pass I have a wheel that produces 33 pulses per revolution. The RPM of that wheel will be anywhere from 25.21 to 62.7 Pulses...
4,704