Hey guys,
Been a while, I have an odd one. Something that should be straightforward.
I have a 1769-IF8 module, looking to add an analog, been in operation for couple years.
I have 6 single ended inputs working on input 0-5 with no problems. With those I obviously have the jumper in place to ANLG COM.
I am adding a 4-wire device to 7th input. This requires connection to Iin 6+ and V/I in 6-. Seems pretty straightforward.
Doesn't work. I moved it to the 8th input, same thing 0mA. I am 100% sure that the ANLG common jumper is not in place.
I moved on of the single-ended inputs onto one of those (with jumper) works fine.
I measure the current inline, 4 mA as expected. When I unpair my remote device, drops to 1.8mA as expected.
Tried 0-20, 4-20 etc.
Also worth noting, when producing 4mA, I see about 1V across terminals and 0.47 at the 1.8mA which correlates to the 250ohm load of the card.
Nothing ever reads into Local CH Data register.
Thoughts?? I'm stumped.
Been a while, I have an odd one. Something that should be straightforward.
I have a 1769-IF8 module, looking to add an analog, been in operation for couple years.
I have 6 single ended inputs working on input 0-5 with no problems. With those I obviously have the jumper in place to ANLG COM.
I am adding a 4-wire device to 7th input. This requires connection to Iin 6+ and V/I in 6-. Seems pretty straightforward.
Doesn't work. I moved it to the 8th input, same thing 0mA. I am 100% sure that the ANLG common jumper is not in place.
I moved on of the single-ended inputs onto one of those (with jumper) works fine.
I measure the current inline, 4 mA as expected. When I unpair my remote device, drops to 1.8mA as expected.
Tried 0-20, 4-20 etc.
Also worth noting, when producing 4mA, I see about 1V across terminals and 0.47 at the 1.8mA which correlates to the 250ohm load of the card.
Nothing ever reads into Local CH Data register.
Thoughts?? I'm stumped.