1769-of8v configuration
ravirajan
Sep 2015
Dubai
I am using 1769-OF8V Analog output module in 1769-L32E compact logix system.
Output is not generated from this analog output module. Status "OK" LED flashing green. how to rectify this problem ?šŸ™ƒ
Welcome to the forum!
A quick google search turns up the manual for this card, which tells you that a flashing "OK" LED means external power failure. This card can be powered from the backplane, or from an external power source. If your OK light is flashing, it's obviously selected to external power, and there is no external power.
And here's the page showing the switch which selects bus power or external power. Although I would suggest that if this problem has only just presented, you should investigate the loss of external power further rather than just switching to bus power.
Thank you
It works.
External power supply problem was there. I just looped 24v positive and negative from nearby module and it is working.
šŸŗ:geek:
Good Afternoon , I'm going to be replacing a few SLC 500 PLC's with CompactLogix this year. I would like to keep the PowerFlex 70 Drives in...
2,128
Hi Guys, I have a fault with a 1769-OF8V that has been in service now for over two years. The data is going to the outputs on the module when...
1,514
Does anyone know where, exactly, the configuration file for a 1769-OF8V in slot 1 of a MicroLogix 1500 would be? I have the 1769-UM002B-EN-P pub...
20
4,930
A simple question when I use the external 24VDC suppy to 1769OF8V analog output card, is it ok to bridge the ANLG Com and the dc NEUT.
2,036
Hello hope everyone is doing good. I am having some problems with an RSLogix 5000 project I am working on. I have a 1769-OF8V output module that I...
6,303