1794-aentr - Device ring redunadancy - detecting link down
matt_sd
Jan 2007
Australia
96
Hello I have a network of 1794-AENTR (ring redundancy), all is working ok and I can see when the adapter comms fails (by the GSV looking at the fault code associated to the adaptor), but no way of detecting when one of the 2 ports has failed (i.e the link light off and cable disconnected). The network redundancy works but how can I tell a link is down and we no longer have a ring?
At a basic level, you can use a MSG instruction to a Ring Supervisor to pull out the diagnostic information: "Verify a Fault Location". It does not tell you what ports on the Supervisor are inactive, but more which nodes were last active on port 1 and 2. In other words, you can tell from the IP address of the last active node on port 1 and 2 how far the link is reaching down the chain of nodes before the ring is broken. To determine, programmatically, where the physical break in the ring is, you would have to know the layout of the ring address wise so as to flag which link section is down.
At a more advanced level, you can use a MSG instruction to all and any Supervisor capable nodes to pull out their status and diagnostics info. This info includes, among others, the above Fault Location, Network Status (Normal, Fault, etc.), and Ring Supervisor Status. The Ring Supervisor Status will tell you if a Supervisor is currently an Active Ring Supervisor or a Backup Supervisor. This, along with the Fault Location, can be further used to determine where in the physical network a link may be down.
Have a look here at Chapter 3:
Publication ENET-AP005: EtherNet/IP Embedded Switch Technology Application Guide
Any questions, fire away.
Regards,
George
Also see here...
548091 - Verifying DLR Fault Location in supervisor Network tab
Access Level: TechConnect
...and here...
452172 - Device-Level Ring (DLR): Diagnostic Information, Retrieving Programmatically
They are basically outlining the methods explained above and in the PDF I linked.
Regards,
George
Hi Guys, Just observe something regarding the V30.01 Studio 5000 software I'm using. The 1794-AENTR firmware available only on the configuration...
2,219
We have a DLR network with a few flex IO racks. One of the 1794-AENTRs is faulted with code 16#0106, which does not make much sense being a DLR...
2,221
Hello We are having communication problems when we lose power. As you can see on the picture we have 1794-AENTR connected to STRATIX 2000 which...
2,089
Hello everyone. I need some help on Studio 5000 (Logix 5000). I cannot add a new FlexIO module. See prints. I need to add 1x 1794OE12 1x...
1,778
Hi All, Had a strange one today, managed to get round it, but searching for a possible explanation...not found one yet... We took a ControlLogix...
3,161