1794-AENTR fault code 16#0106
jefforshoski
Jun 2016
Kansas City
We have a DLR network with a few flex IO racks. One of the 1794-AENTRs is faulted with code 16#0106, which does not make much sense being a DLR network that only has one controller. The 1794-AENTR also shows Internal State: Program Mode. The connection is unicast. I have worked with many 1794-AENTRs and don't recall ever seeing something like this. The controller is for a furnace, so there are not too many things we can do since we run 24/7. Any ideas are appreciated.
Welcome to the forum!
My quick search of the knowledgebase did show up one technote on a 1794-AENT, where this error was caused by a duplicate IP address. If it were me, the first thing I'd do would be to note the IP address of the fsaulted device, remove it from the ring, connect my laptop into the ring, and see if I can still ping that address.
code 16#0106 is "Connection Request Error: Module owned and configured by another controller". Could it be that the PLC was changed and the
1794-AENTR has not been power cycled and it is remembering the previous owner? Is it possible to power cycle this one 1794-AENT?
Thank you both for the replies!! I will see if we can get a chance to power down the AENTR to ping the IP address. And the power cycle is what I wanted to try since we just had a power glitch last week and maybe it did not come up correctly. I have tried to uncheck the unicast connection since everything is inputs on the bus, but that did not change its status.
Hi Guys, Just observe something regarding the V30.01 Studio 5000 software I'm using. The 1794-AENTR firmware available only on the configuration...
2,217
Hello We are having communication problems when we lose power. As you can see on the picture we have 1794-AENTR connected to STRATIX 2000 which...
2,089
Hello everyone. I need some help on Studio 5000 (Logix 5000). I cannot add a new FlexIO module. See prints. I need to add 1x 1794OE12 1x...
1,778
Hi All, Had a strange one today, managed to get round it, but searching for a possible explanation...not found one yet... We took a ControlLogix...
3,158
First of all, I'm new to Allen Bradley. Have almost exclusively worked with Siemens before. I'm trying to add a new IO station to the my...
5,887