Hi, Can anyone help me? I have limited space on a flex I/0 rack and wanted to use a 1794-OE12 but am not sure this is compatible with PLC 5 / RSlogix 5. In the I/O Config the OE12 is not listed. Do I need to update RSlogix? or is it only compatible with control logix?
 
Welcome to the Forum!

Yes it is possible, but you have to Manually Configure the Block Transfer. The steps are outlined in AB/Rockwell Knowledgebase Article 66453. It is quite lengthy, so I haven't tried to replicate it here. Also, be aware the OE12 requires a different base. I think it is a TB3G if memory serves.

Stu....
 
Last edited:
Hi Stu
Thanks for your answer. I had the block transfer OK but wasn't able to configure the channels to 4-20mA. But was very easy after reading the above mentioned Knowledge base article.
Thanks Again
Eleco78
 

Similar Topics

Hello! I have a problem with ControlNet... I have a ControlNet wich consists from 7 flexbuses. In one FlexBus I need change AO module 1794-OE4...
Replies
1
Views
1,675
Hi Friends, I'm facing problem in 1794-oe12 flex i/os. Im not getting 4-20ma output. i hope its a self powered. only module supply...
Replies
12
Views
14,389
what magic do i need to do to get the 1794-oe12 analog output card to give me my 4-20 ma it was configured to do. i am using a rslogix5000...
Replies
1
Views
2,313
I am having issues locating the status codes and figuring out why I don't have any output from my analog output card. Here's the configuration as...
Replies
7
Views
4,883
Hi I installed 1794-OE12 flex IO, the module power LED starts blinking, then I turned ON the module enable bit and resetted the Wire Off reset...
Replies
13
Views
26,749
Back
Top Bottom