1796-it6 programming
jgrassel
Apr 2014
Austin TX
18
Hello all,
I'm getting to know (reacquainted, really) with the Compact I/O line from AB. I've got at TC module (1796-it6) up and running with my L35E processor. I tried configuring it to give me engineering units from a Type K TC (pretty basic) but for some reason it reads 707 at room temperature. I chose Engineering Units X1, Degrees F, Type K. And when monitoring it online with something such as a move instruction, the number I see is 707 and it goes up to about 900 when I hold it for a few seconds. What am I doing wrong?!!
Thanks a lot!
It seems like my changes are being applied, I think. Meaning that if for example I change the engineering units from C to F, and apply the changes, I start seeing a different number flowing into the online monitoring of the ladder logic (still a weird number, but definitely something live and moving when I touch the TC).
I think the units for these modules are 1/10 of a degree.
So "707" is 70.7 degrees F, a comfortable room temperature.
Makes total sense...sort of...since there is a configuration options to display engineering units X10. !! I shoulda thought of that. Thanks a lot!
I've always found that X1 vs. X10 configuration option confusing in AB TC modules. It seems backward to me. I would expect straight up Degrees with the X1 option and Degrees times 10 with the X10 option. Oh well...
I have a relay output card that keeps having issues but with different relays. Every couple of weeks or so, an output relay will energize but will...
2,204
Hello all, I ran in to some trouble. I created 2 virtual machines to try out ADS communicating One machine is a PLC (TC2 32bit (runtime)), other...
20,164
Hi everyone. New to RSLogix5000 and learning as much as I can. I'm much more familiar with Omron. Is it required I select "scaled for...
1,845
Anyone know a fix for this? 1769-IT6, 2 modules both have same problem. Setup for K tc, 1x engineering units data, degrees F, 60Hz filter...
4,263
Using a 1769-IT6 module with a Type K thermocouple, we're seeing a +7 degree C offset. We used a calibrated fluke tester and simulated both 0C...
2,758