Relay getting stuck closed 1796-OW16 module

sh281986

Member
Join Date
Sep 2022
Location
Texas
Posts
6
I have a relay output card that keeps having issues but with different relays. Every couple of weeks or so, an output relay will energize but will not de-energize. I'm not really given enough time to troubleshoot the machine so I just put another module in to keep it running for a few more weeks until the issue inevitably happens again. The OTE in the program shows that it should not be energized but it is. The output terminal shows 24VDC and that reading never goes to zero when the output signal should be off. I checked the incoming voltage and its around 24vdc. All of the connections are tight as well. Does anyone have any advice for me on why the relays keep failing? Thanks.
 
I think the first thing to check would be the current draw of the loads controlled by the outputs, both the holding current and the inrush. If you're switching inductive loads, you'll improve contact life by adding surge suppressors. Relay contact outputs are generally rated by holding current capacity and don't have as much margin for inductive 'kick' as solid state outputs.
 
The diode shown on the page in that manual is across the cards internal relay coil, not the output terminals.

25W solenoid is a big boy. I would personally use an external interposing relay to drive the solenoid and fit that with a flyback diode across its contacts, as Steve Bailey said.

I normally only deal with 8W solenoids at 24VDC that cycle probably once every 10-30 seconds. We would destroy 6A relay contacts within 9-12 months. Replaced them all with solid state relays and fitted flyback diodes, no issues for the last 3 years.
 
i see two issues that you have.
1 the relay outputs have a lifespan, typically 600,000.
how often is the output cycled?

2. you need to put a reverse bias diode in the load side of the output to keep the reverse voltage from basically arcing and welding the contacts.
a 25 watt / 24 volt solenoid draws 1.04 amps once it is energized in a steady state. BUT, in my experience, the surge current can be 6-10 times that or 6.25 amps if it were 6 times the steady current.

you might try a solid state output card if they make them, and also add the reverse bias diode.
regards,
james
 
As above, I would recommend a small interposing relay installed. They're a couple of $ a piece and far cheaper an easier to replace if they end up burnt out than an output card.

Secondly to monitor that the output isn't being driven on an off in rapid succession. Chattering an output on an inductive load will shorten the life span dramatically.
 
The relays energizes 24vdc coils which opens a solenoid valve. Would these require surge suppression?
Yep. These can be some of the worst. Look at the size of the solenoid. If it is big, it will be a large induction.
Just be used to add surge suppression to any large coil, that be relay, contactor, valve or whatever.
 
2. you need to put a reverse bias diode in the load side of the output to keep the reverse voltage from basically arcing and welding the contacts.
a 25 watt / 24 volt solenoid draws 1.04 amps once it is energized in a steady state. BUT, in my experience, the surge current can be 6-10 times that or 6.25 amps if it were 6 times the steady current.
I have never seen a socalled reverse bias diode on a PLC output.

Also, it is more the induction that is the problem, not only the current value itself. Think of the current flowing as a wheel spinning and the induction being the mass of the wheel. A light wheel can be stopped by a person grabbing the wheel with the fingers whereas a heavy flywheel can shear the teeth of gears if you try to stop it instantly.

A 'freewheeling' diode for DC coils is like a directional ratchet clutch. The current will flow until the energy as dissipated in the same a wheel would spin until stopping by internal friction. So that can mean that the turning off will take longer time.

An RC snubber is like sticking a rubber plug in the spokes of a wheel. The stopping will be more violent, but essentially instantaneous and less violent than just stopping directly. Works with both AC and DC.

A varistor is like a friction clutch. Somewhere between the two above. Works with both AC and DC.
 
Any reason he couldn't add small interface relays between the output and coil?

This is typically what I would do although depending on the number of inductive loads the relays could be more expensive.
 

Similar Topics

Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
110
Hello, I need assistance in making a Relay operation that follows the given parameters: -if S1 is switched and S2 is at off, the Lamp 1 will be...
Replies
3
Views
111
Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
Replies
14
Views
437
I have an application where I want to use a safety relay in combination with a flame detector as the sensing element. The flame detector has relay...
Replies
23
Views
1,080
Back
Top Bottom