18 pulse VFD vs the active front end drives?

TheWaterboy

Lifetime Supporting Member + Moderator
Join Date
May 2006
Location
-27.9679796,153.419016
Posts
1,931
Anyone have any good or bad experience with the 755 series drives from AB that have the Active Front end?
I have to approve something for 3 projects coming up and I want to give these drives a shot unless someone can tell me something to watch out for that would change my mind.
 
Anyone have any good or bad experience with the 755 series drives from AB that have the Active Front end?
I have to approve something for 3 projects coming up and I want to give these drives a shot unless someone can tell me something to watch out for that would change my mind.
I've found them reliable but about double the cost of comparable drives from other manufacturers.
 
My experience with active front-end drives from various manufacturers has been good. I think 18-pulse is obsolescent technology.
 

Similar Topics

I'm looking for recommendations on a VFD that will act more or less like a servo or stepper drive. I have an induction motor with encoder, and...
Replies
16
Views
5,926
Hi Everyone, Like the title says I am looking for opinions on the Automation Direct DuraPulse AC Drive. In the past I have only use AB Powerflex...
Replies
7
Views
4,662
Looking for input I was looking at a durapulse drive 5hp to use on a cut to length application. cuts will be 10 to 18 inch long. Any ideas I know...
Replies
4
Views
2,924
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
177
Hi All, I'd like to know can we use DTR instruction to get a week pulse ? Could anyone please help me to understand that one ? I've managed to...
Replies
4
Views
190
Back
Top Bottom