hai all..
recently i had facing problem with sew euro drive motor(2.2kw rated amp 4.95
415 voltage.
this motor c/w gear motor to drive screw conveyor ..
problem is the motor get Burn and overload didnt trip. where by the overload
is set to 7.5amp..as i told to MCC supplier this motor overload is to big to trip
but than they argue saying it correct..i had try calculate as the rated amp X 115% also didnt reach to 7.5amp. that why it didnt trip ..they say i m wrong
and it should trip .but the fact it didnt ..
had i make mistake on calculation using 115%.. i been using this formulation for many years.
freeload this motor running is 3.1amp.
i had check mechincal part such bearing .gearbox and even screw conveyor .
all seem okay and no damage ..