I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped L2 back thru L3 to keep them balanced.
Is there a better or cleaner way of doing it? A standard 3 pole contactor and MPCB?
The few times I've dealt with single phase motors, we did the overloads/MPCB the same way looping L2 back through L3. Most equipment OEMs we've dealt with have also done it that way. 🤷‍♂️
That's the way we have done it for years. Just looking to see if anyone else had a different idea.
Just for some clarification for future readers:
The reason for looping the conductors back through the starter is that many modern electronic overload devices have a detection circuit for phase imbalance (current is typically >5% different between phases) or a phase loss detection, both of which will trip the overload.
To the OP: further clarification, these motors are not the normal single phase thermally protected types, correct? They do in fact require a starter for protection?
As long as it is a motor with easy starting, it will work well with a standard MPCB, but if it carries a load with more inertia such as the turbine of a fan, it is better to use overcurrent protection and a separate thermal protection relay coupled to the contactor, since you can choose one of class 20 or class 30 that allows a longer starting time due to the low starting torque of those motors. Always using L2 and L3 in a loop.
A true single phase motor overload would have 2 poles.
Imagine the engineering and production costs to put one on the market - a 3 pole one would be a lot less expensive. and is readily available.
I have seen on older panels a single heater type overload, but for a single phase of 2 line leads that leaves one lead unprotected.
I have also encountered German machines with single phase motors and heaters where they only run one line through a circuit breaker, a single pole contactor like home air conditioning units, and then run the second line (not grounded neutral) straight back to the service disconnect so that line is HOT at all times and the heater/motor runs of the controlled line grounds out and trips the breaker.
https://www.grainger.com/product/SQUARE-D-Manual-Motor-Starter-Non-Reversing-1H416 for $588 USD, comes with a box!
What would happen if you ran a 60Hz Single Phase Motor on 50Hz supply?
584
Hi PLCs.net! I'm working on a multi-motor system, most motors are single phase, driven by servo drives. I wanted to check what kind of motor...
1,587
Any panel I've built with contactors and overloads has been 3 phase. I'm now quoting on one with some small single-phase loads. Definition of...
24
5,864
Hello everyone, I ran into this 230 single phase two speed motor with two capacitors and a relay (see picture) and have a few questions: The...
1,441
Good Morning , I should know this , but will a 3 Phase overload trip if a 3 Phase motor runs single phase for a long period of time ...
2,243