60Hz Single Phase Motor on 50Hz supply
It will run slower. And draw more current. And overheat the motor. Shouldn't do it.
It will run slower (cca 17%).
I will draw little bit more of current (not over 4-5%) with constant torque loads, with fans it will substantially reduce power/current consumption .
It will not overheat the motor, at this frequency. In fact, from my experience, from 25Hz and above, in normal circumstances, you don't have ventilation problem.
It is not dual rated. It is single phase rated for 230v/115v 60Hz. I don't have 50Hz but I'm sending it to 50Hz-landia.
I'm worried about the capacitor and startup circuit frying the thing.
Most of 50Hz lands are 400V(3-phase)/230V(single phase), and usually TN-C/S grounding or in fewer cases TT grounding.
You need to make sure that it is compatible. In most Europe, three phase is preferred, almost obligatory in industrial plants.
When my company supplies equipment, if it is not specifically required by customer, the electrical enclosure will have on input 3 phases and Protective Earth, without Neutral and there will be 400V/230V transformer for control voltage, so there will be no way to connect single phase motor.
I have a (*) PowerFlex 525 being supplied with 400VAC, 60 cycle, 3-phase. This is not a type-o, this is accurate. Now, the drive clearly states...
1,181
the age old question / issue a friend has bought a 1000watt 120vac 60hz rated appliance from the USA into Australia (which has a 240Vac 50Hz...
2,448
I'm located in Australia, my potential client has some equipment recently delivered from USA rated with a 480Vac 60Hz Supply i assume it's 3 Phase...
4,177
So I'm running into a strange problem with a new Powerflex that was installed on an existing conveyor. When the commanded frequency approaches...
14,432
We are shop testing a system that is being shipped to a location with 380V @50Hz. All of the motors are rated 190/380V (jumpered for high...
2,714