2 Powerflex 525's to micrologix 1100
AA_Ron
Feb 2016
Minnesota
43
Hey all,
So I have a project that i'm trying to connect 2 powerflex 525's to a micrologix 1100 plc. I would have liked to use a compact logix but cost is a factor. So I currently have 1 drive connected and being controlled but the second drive will not connect. I verified that Ethernet on both it does work. but the second drive still will not connect. I think it might be the timeout bit N42:3 I have that bit set up for both drives in my program. is there another timeout set I can use or is this pretty much a sunken ship.
What, exactly, do you mean by "will not connect" ?
You will need two separate MSG instructions for these drives. You can use the same source data table element when you write to N42:3 in each drive, but the MSG control data elements (MGx:y) must be unique.
Post some examples of how you are triggering the MSG instructions, and what kind of error codes you are getting.
Thanks for the quick response, yeah I had used separate messages in my plc program to run the drives I/E m9 file element and m13 file element. I will take some photos tomorrow of what I did exactly. The first controller I did at 192.168.240.3 and the drive was connected and I could control it through the plc MG9. the second drive 192.168.240.4 would not connect using MG13. I also separated my RI files in this program. if you have any program examples to run both drives that would be amazing.
Yeah for sure man I put the hop in. I did end up finding the problem. the integer N11:0 needed to be set for both drives. once I set that the drive connected. The picture has what I needed to change on it for reference. thanks a bunch brothers appreciate your words of wisdom.
I am controlling a powerflex 525 over ethernet with micrologix 1100, I have the drive set up and running forward and reverse, I would like to...
2,854
I am controlling a Powerflex 525 drive with a Micrologix 1100 through explicit messaging. Just the basic start, stop, and speed control. Reading...
2,394
PowerFlex 525 - can you access the parameters from a MicroLogix 1400 & CompactLogix Good Morning , I have a separate stand alone machine...
3,338
Hello All, I am using the on-board PID on a PowerFlex 525 to run a conveyor that will maintain a loop using a distance laser. The laser is hooked...
8,643
Hi all, Great forum first time at posting. Have been searching but can't find any info on the above subject. I have set IP adrresses in PF525 and...
6,707