2 wire analog sensor power supply issues
Kataeb
Jan 2007
www.livelovelebanon.com
636
The 4-20ma sensor will act just a "Voltage Regular" as long as the voltage is between it's recommended value the output will remain constant.
Example: If you are using a 24 vdc external power supply to power the sensor and it is measuring an output of 10.5ma that value will not change as long as you stay within the recommended supply.
Just like a "Voltage Regulator" if you are using a 5 vdc regulator the input can be between probable 6vdc and 24vdc but the output will be regulated to 5 vdc!
I'm trying to recall if I ever traced a noise issue to a DC power supply, and I can't recall one, and my experience goes back to older linear power supplies and the newer switch-mode power supplies (SMPS). I've used really cheap wall wart SMPS for short duration tests and setups and haven't seen a problem. Permanent panel jobs are all industrial 24Vdc supplies nowadays that have (remarkably) limited ripple.
A far more common cause of noise in 4-20mA circuits is VFD generated noise
http://www.eng-tips.com/viewthread.cfm?qid=419481
Here's a link to a discussion about the shield-connection-to-ground causing noise on a 4-20mA loop
http://www.plctalk.net/qanda/showthread.php?t=88718
Noise from a DC power supply can cause a problem with HART communications that runs on the 4-20mA current loop. HART spec includes spec of maximum ripple 0.2V p-p, Maximum noise at 500Hz to 10KHz of 1.2mV rms and a maximum series impedance of 10 ohms for the same frequency range as the max noise.
Good white paper on 4-20mA noise from Precision Digital:
https://www.predig.com/whitepaper/reducing-signal-noise-practice
No there will be no effect on the signal, however as it can be also used for the reference inside the PLC it could be a problem inside the PLC.
Hello everyone, I'm new to the forum and I've never work with analog sensors before. How do I wire up 3-wire ultrasonic analog sensor to Allen...
2,003
Hi, Is it possible to connect 2-wire sensor and 4-wire sensor together in an analog module of a PLC, where COM terminal is only one single. For...
20
17,018
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
265
Hey folks, Hardware: *=Must use these devices. Allen Bradley 1734-AENTR (Dual Ethernet Adapter)* Allen Bradley 1734-IE8C (8Ch Analog Input...
706
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,136