20-comm-e Powerflex drive and Datalinks
pauly
May 2002
South Wales,U.k
244
I am using a powerflex70 with 20-comm-e to controllogix L55 version 16. How do you use the datalinks to transmit and receive extra words? The default tags are created automatically how do you access the data links from within RSLogix?
On the General Tab for the drive properties, click on the Change button for the module definition. Define which datalinks you will use and what parameter you wish to tranfer,click on OK. The tags for the drive should be updated.
Mike_RH is right on; in v16 is easier than ever to reconfigure DataLinks for drives connected using ControlNet or EtherNet/IP.
In the General Tab of the drive's I/O Module configuration window, click the "Change" button in the Module Definition section:
I had to replace 3 PowerFlex 40 multi-drives that each had 3 PF4M daisy chained off the DSI port. The PF40s had comm-e cards installed for...
2,445
I am trying to commission a 480 vac PowerFlex 40 (22-COMM-E) in my home office ( I have 208 VAC hooked up to L1 and L2 . 120 VAC was not enough to...
2,494
I have 3 new PowerFlex 7000 VFD's. Rockwell was out to do some checking before startup. These are part of a larger electrical project. I gave the...
337
Hello all, new here. I have 16 Powerflex 40’s that I am converting from DeviceNET to Ethernet. I changed all of the Comm modules to 22-COMM-E and...
1,129
I've been talking with PowerFlex 525 Drives using the Comm C module with a non rockwell controller without any issues. I went ahead and loaded...
1,032