We are in the process of upgrading our PLC-5 to a ContolLogix. Our system has a couple of control panels that use the Bulletin 2705 RediPANEL and DL40 Dataliner.
Question: Can the RediPANEL and DL40 be communicated with on a ControlLogix with just the 1756-DHRIO module, or does it need to interface with legacy equipment?
I can't seem to find any literature on the matter.
Cheers
Nick
Nick, if your devices have a RIO connection available, there isn't problem to connect them to a CLX thru a -DHRIO card.
RIO is always the same in every platform (PLC - SLC - CLX)...
This is a LINK to a KB note from Rockwell, with some indications on how to get a DL40+ works with CLX via DHRIO.
Basically your devices should be configured as "Generic Remote I/O Adapter" under the DHRIO card.
Hope this helps...
- [font=comic sans ms,sans-serif]fuzzy logic[/font]
Thanks Fuzzy,
I have read somewhere that RediPANELs incorporate 1771-ASB electronics inside. Does this mean that for the RediPANEL, I should select the 1771-ASB under the DHRIO tree?
Since the panel is a combination of I/O and RIO, after configuring a RIO adaptor do I add digital I/O modules to represent the pushbuttons and indicators?
Thanks again
Nick D
Fuzzy,
I found that link a couple of days ago and it cleared things up, thanks.
I set up a program using the generic adaptor instead of the 1771-ASB and it seemed to work fine. Do you know if, by doing so, I have allowed for possible errors later down the track? In other words what effectively is the difference between them.. if any?
Cheers
Nick
Nick, I think you will have not errors on that.
Using RIO, there is no differances between the 1771-ASB or Generic profile... if you see there is not an Electronic keying for those modules.
RIO is based on hardware, only important things are Rack/Group/Size attributes.
The Catalog number is only for program documentation.
Cheers.
We recently sent out a couple RediPanels back to Rockwell to get the displays and keypads replaced. We have four panels that we use all the time...
1,609
Hello, I have a machine that has a AB 2705-K11C1 keypad Redipanel connected to a 1771-SN scanner board. Installed on a PLC-2/02 (1772-LZ D)...
1,645
Hi I'm working on replacing some old Redipanel terminal's and i need to find something to work with a PLC5/20 on RIO protocol. I already made a...
3,063
112
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
110