4-20 mA Cable and RS485 in Same Conduit?
elitheei
Nov 2004
Atlanta
81
I got to make a run of 4-20 and RS485 of Belden cables. Can I run both of these in the same conduit? The run is about 500 feet. This may be a dumb ?? for some of you guys but rather be safe than sorry. Thanks in advance for your help.
Thanks, I was fixing to write a PO then i got tho thinking .... Is this OK? It's tuff getting old, twenty yrs ago I could remember everything now I barely make it to work some days! If wasn't for message bds I would have to retire!
Thanks again ...!
24 VDC & 4-20mA
Correct me if I'm wrong here. :)
Now I've heard its a common practice to separate 24VDC & 4-20mA into different conduits, even though the 4-20mA is running at the 24 Volts.
I've also remember reading the NEC book stating that when running signal and power conduits parallel; there should be a certain amount of distance between them incase of interferences.
The only real need is to separate AC and DC cables, especially anything over 120VAC.
DC @ 24v doesnt have enough current to cause any significant noise issues, especially when most comm cables are shielded anyways.
With such a long run should he consider breaking up metal conduit, or run pcb conduit, to prevent any coupling issues in case it runs by anything with higher voltage?
Any benefits from adding a terminal strip halfway?
Metal conduit could be a consideration I've done longer 4-20 ma runs through electrical rooms with no problem using belden cabling without any noticable problems, adding a terminal strip would not help
We keep our AC separate from our 4/20ma, both in conduit.
No issues with comms wiring and 4/20ma--both low voltage and, typically, shielded cabling.
I am going to daisy chain a couple Modbus devices off of a Click plc using rs 485. There will be three slave devices daisy chained off one another...
16
9,240
Hi all, I'm trying to get a bom together for an R&D project. I have modbus devices that require 355mA for power plus communications. Does anyone...
1,319
Hi, How do people terminate cable screens on RS485? I've been reading around and people seem to do various things. A few people have said you...
2,563
Hi I have been reading stuff online about the "characteristic resistance" of cable which is best for RS485. A lot of material says you should...
2,777
dear everybody I'm not yes USB to RS485 converter cable, types: USB to RS485 converter cable connecting for plc siemen S7 300 and S7 200. to...
3,352