I am using a siemens output module and I saw that there is also 4 wire diagram for voltage output.
Is there anyone who can explain the reason of 4 wire insted of 2 for voltage output ?
Thanks in advance.
It could be for voltage drop compensation. I can't remember exactly but it may measure on one set and use that to adjust. I may be completely wrong but seems to ring a bell. I may be confusing it with a process transmitter
But the OP is asking about a 120v output.
I read only "voltage output" and since it's about the difference between 2 or 4 wire I assume it's about an analog voltage output like 0..10V
I think what SD_Scott posted is about what OP asked.
Still it is not entirely clear to me why to use 4 wire. is it to overcome and detect things like wire break?
In a current loop the current stays the same as long as the loop doesn't exceed a certain impedance. In a voltage loop the transmitter needs to compensate for the lead resistance and in a 4 wire setup it can compensate for lead wire imbalances also. Not sure what OPs output card is though. Hope that helps.
thanks.
the siemens card can probably be set-up either as 2 or 4 wired and from my mind also voltage or mA can be chosen
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,144
Hi, May i know the how to know the minimum voltage to drive a analog input card. I'm connected to 4-20mA channel for 4 wire, supply voltage from...
6,655
Does anyone know the color code for a 4 wire dc device. I'm pretty sure brown is for +24vdc, blue for 0vdc. As far as black and white i'm not sure.
19,022
When you have PT100 Sensors connected in 4-wire, then u transfer a measurement to the PLC, when u use 2-wire, the PT100 works like a resistor...
7,953
I was called out to look at a machine, where the customer was complaining about voltage spikes on the ground wire going to an ampliphier card. I...
26
15,519