480V heating element control
Snap25
Dec 2014
Michigan
237
I have a few tanks that each have 6 heating elements. I'm trying to figure out the best way to control them..
1, They each have a contactor in the control panel and I can gain better control of the temp by turning on/off individually as the tank temp deviates.
2, One contactor rated for all 6 elements combined.
3, Any other ideas?
Let's think this through before putting in an scr / triac.
the scr controls require that one leg of the system be on at all times.
I cannot say for sure about the triac.
in either case, you have a tank and when the power is turned off on a contactor, there is no leakage unless a contact welds.
with electronic controls such as the triac and scr, you can have current leakage.
if an scr or triac goes bad in the on position, how will you turn the power off?
We do NOT want any chance of electrical current in a tank getting to others.
I would recommend a mercury contactor rated higher than your contactor.
no contacts to weld or contactors to replace.
if I am wrong, someone please correct me.
james
james
You can get scr with 3phase control I believe. Either way, you would want a contractor ahead of the scr that is part of the enable/overtemp/safety circuit. All would need to be good to go to turn on the contractor that sends power into the scr.
...you would want a contactor ahead of the scr that is part of the enable/overtemp/safety circuit. All would need to be good to go to turn on the contactor that sends power into the scr.
+1 for contactor. It's a must.
The 3 pole Crydom is fine, but pricy. With three phase, you only need to control two of them. Two single phase SCRs would be fine, along with the contactor of course.
Edit: Size current rating of SSR at 3.5x the heater current. For the 25 Amp Crydom, the heaters should only draw a maximum of ~7 Amps per phase.
Are all 6 elements the same size?
If you want 0-100% power control you would only need SCR control on one of them the rest can be switched, or rather I should say that each of them has a contactor and one of them has an SCR after
So a contactor for all 6 and a SCR on one heating element (after the contactor)?
Toggle the other 5 heat elements at different deviation stages and use the SCR to maintain?
I would do 1 large contractor feeding 1 large scr feeding all of the elements. I would have fusing ahead of contractor for total load, and each element fused after the scr. This all assumes that the size of the elements makes this economical. If the elements are large, then it may make more economical.oval sense to split them into groups of two or three, each with contractor and scr.
I only have to control 2 out of the 3 legs? The other one is live going to the heating element?
Yes that is one way that most 3phase scr work. You need the contractor ahead of the scr to completely remove all power from elements.
Hi Everyone, Got a "Oh by the way" added to my latest project. They want to add 480V 12KW Heater to one of the tanks. Since I have never done a...
4,710
Hello all... I'm looking for a 480v 3ø 25+ amp Solid State Relay to replace a mechanical one beating itself to death keeping temp in a heating...
1,990
I know with larger motors you do not want them to start with a contactor above 30HP or so because they will 'sag' the power in the plant and the...
831
Abb acq580 75hp on a deep well pump. 500' of motor leads, 110A TCI V1000 output reactor/filter on drive output leads . Service is a 3 phase 3wire...
1,260
This is a odd thing to ask and I'm sure it's not allowed, but I'm curious about the problems and effect from taking g a 480v Delta system (no...
21
6,184