500-5051 Thermocouple module manual

dhofstetter

Member
Join Date
May 2009
Location
Denton NC
Posts
15
Hello,

I have a module that has lost factory calibration settings.

I need to go through the self calibration procedure.

I'm pretty sure its just one page out of the manual that explains
what voltage to apply (mv) during which part of the calibration procedure..

Thanks...

Duane
 
500-5051 Manual

Lancie1,

No its for a Siemens / TI 500 series 500-5051.

And I did receive a PDF copy of the manual from another
forum member for this..

I should have updated this thread to solved..

Its actually several steps with this module as you
first calibrate to 0mv

Then each 10 18 36 and finally 45mv.

This is stored in a 2212 NVRAM chip.
This chip was scrambled so we had to start from scratch.

Thanks for the reply..

Duane
 

Similar Topics

Good day: I am wondering if anyone has experience with the Kinetix 5500 S33 Fault. I have 3 drives in a group set as follows: 2198-H025-ERS2...
Replies
4
Views
93
I recently did a program conversion from logix 500 to studio 5000 and when machine runs it depends on two ton instructions to keep the machine in...
Replies
17
Views
489
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
15
Views
277
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
101
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
114
Back
Top Bottom