This is a new one to me. We thought we were having sensor issues when trying to commission a new machine, but realized that the inputs were not lighting up on the 5069-IB16 despite there being 24vdc at the terminal. I was able to isolate this to when one of the conveyors (1/2hp motor) was running. The signal wires are not run near the VFD power wires. The moment the VFD stops, the signal inputs indicate correctly on the module (and in the PLC code). Even more odd, this only seems to affect one of the two IB16 modules, leading me to believe maybe there is something wrong with the card. We have bonded everything and ensured good grounds on this relatively small machine and running out of ideas. I will be back with this customer on Thursday and will bring a spare 5069-IB16 module, but I'm not entirely hopeful.
Electrical gremlins like this are tough!