5069-OBV8S/A Safety Output card
PreLC
Apr 2019
Mars
587
Hi PLCs.net!
I had some questions about using the Safety Output Card, I have aL310ERMS2 with V32 in it.
I have tried to use the PLC to energize the Local:3:O.Pt00.Data boolean using OTE, but that has not helped.
LA Power is connected properly. The output pins have no connection to them.
When I put a multimeter on the card, I'm getting a pulsating output I THINK. I don't have an oscilloscope in my lab, so it's a little limited.
Does anyone know how to properly configure the PLC Tag?
Attached are the screenshots:https://imgur.com/9vssOAu
https://imgur.com/JQLcVTg
https://imgur.com/fKl3cx9
Thanks!
-PreLC
This was the situation that I had where there was a spare safety output on my rack and I decided to use for my control power on LED lamp. There needs to be a sufficient load on the output otherwise it detects "Open wire". Try turning on a relay coil instead of empty load, then meter and check it out.
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
110
Hi all, Just a heads up on an issue that a colleague of mine was unfortunate enough to stumble upon recently. The new 5380 Compact GuardLogix...
20
10,072
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
401
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
546
Hi all, have a project which requires reading a weigh head weight over ASCII. Never really touched ascii so struggling a bit. The weigh head is in...
1,243