Apr 2019
Location
Mars
Posts
587
Hi PLCs.net!

I had some questions about using the Safety Output Card, I have aL310ERMS2 with V32 in it.

I have tried to use the PLC to energize the Local:3:O.Pt00.Data boolean using OTE, but that has not helped.
LA Power is connected properly. The output pins have no connection to them.

When I put a multimeter on the card, I'm getting a pulsating output I THINK. I don't have an oscilloscope in my lab, so it's a little limited.

Does anyone know how to properly configure the PLC Tag?

Attached are the screenshots:https://imgur.com/9vssOAu
https://imgur.com/JQLcVTg
https://imgur.com/fKl3cx9

Thanks!
-PreLC
 
This was the situation that I had where there was a spare safety output on my rack and I decided to use for my control power on LED lamp. There needs to be a sufficient load on the output otherwise it detects "Open wire". Try turning on a relay coil instead of empty load, then meter and check it out.
 

Similar Topics

Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
110
Hi all, Just a heads up on an issue that a colleague of mine was unfortunate enough to stumble upon recently. The new 5380 Compact GuardLogix...
Replies
20
Views
10,081
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
Replies
8
Views
402
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
Replies
5
Views
547
Hi all, have a project which requires reading a weigh head weight over ASCII. Never really touched ascii so struggling a bit. The weigh head is in...
Replies
11
Views
1,244
Back
Top Bottom