Trying to switch the grounded leg can lead to problems, and also will cause you to measure erratic and unpredictable voltages-to-ground at the PLC output terminals.
If L2 is your grounded leg and it is connected to COM1 and COM2, then measuring between any COM and any PLC "Y" terminal (with output OFF) means that you are really measuring the voltage through the Output Device connected to that terminal. So this voltage should measure (220 volts minus the voltage drop through the CF Lamp ballast). That explains some of your readings.

I think your PLC outputs are wired backwards.
Our supply voltage is 220 Vac (line-to-line). However, when I tried reading voltage from any PLC output to ground (line-to-ground), I read 100 Vac. This is true even when PLC output is on or off.
Yes, backwards. That is all there is to say about that.
 
Last edited:
Inside many relay outputs there are supressors, so they will give some leakage. If output is open, you will see still voltage with a normal meter.
As these lamps only need very little power they try to start when voltage is high enough, giving small flashes of light.
 
All true, Shooter.

Also, if the Mitsubishi PLC outputs are wired as shown in Ripley's drawing, then measuring voltage "to ground" results in unexpected readings. Shown here by the 3rd reading, 9 to Y1 will not be 0 as might be expected with Y1 off.

Mitsubishi FX2N Wiring Diagram- with CFL.JPG
 
Last edited:
Fortunately or unfortunately, we have a long weekend because its holy week. I may give you an update next week, when we resume to work. BTW, happy easter:)
Easter is fog in the rear-view mirror, and so is April Fool's Day. What happened?
 

Similar Topics

Hi all, Looking for someone that can explain the functionality of the PCFL-INTEG (Integrator) block in a Modicon Quantum 534. I've been...
Replies
0
Views
1,356
If a fixture is rated for 60W, is it ok to install a CFL (Compact Fluorescent Lamp) that claims to give 100W of light for 23W of usage? There...
Replies
2
Views
2,024
Hi I am using Proworx32 1.1 trial version to practise Modicon PLC programming. I have problem of getting any of the PCFL function working in...
Replies
2
Views
4,376
U
Hi friends, I need help to solve one Analoge problem I am using Quantum 11302 CPU using Concept v 2.5 , 984LL logic ACI3000 analog card...
Replies
0
Views
1,854
Unregistered
U
Hi My question related to Quantum PLC usiing Concept v 2.5 Sotware i am using a PCFL -AIN Block in which i am input the Flow data now i need to...
Replies
0
Views
3,172
Back
Top Bottom