If L2 is your grounded leg and it is connected to COM1 and COM2, then measuring between any COM and any PLC "Y" terminal (with output OFF) means that you are really measuring the voltage through the Output Device connected to that terminal. So this voltage should measure (220 volts minus the voltage drop through the CF Lamp ballast). That explains some of your readings.Trying to switch the grounded leg can lead to problems, and also will cause you to measure erratic and unpredictable voltages-to-ground at the PLC output terminals.
I think your PLC outputs are wired backwards.
Yes, backwards. That is all there is to say about that.Our supply voltage is 220 Vac (line-to-line). However, when I tried reading voltage from any PLC output to ground (line-to-ground), I read 100 Vac. This is true even when PLC output is on or off.