Hello everyone.
I am trying to test a analog output, but not getting the expected result.
In the HW conf. the config is current 4-20
in the logic Iam mult the output of a PID (0-100) by 276.48 t0 get 0-27648 and moving that into my output word PQW262.
when the value of PQW262 is CERO I get 4ma,messure acro terminal 3 and 6.
when I increse the value of PQW the ma go down to 1.6ma
Any Ideas about what I am doing wrong
see a couple of pictures attached
thanks
I'm assuming that you have a 15 bit output such that 32767 produces a 20 mA output and .2 x that (6553.4) produces 4mA. So reverse engineering, I would seek to first produce 0 - 26214 (0 - 80%) of 32767 corrosponding to 0 - 16 mA. If your starting with 0 - 100%, then 26214/100=262.14
Therefore your math needs to produce the following:
(Raw Output x 262.14)+6553.4 which will produce your 0-16 mA and then offset it to 4-20mA.
I always model the math in Excel and then save it with the application program. Later, you can take the Raw values and inset them in Excel and it will tell you exactly what the system should be doing.
The kills three birds with a single stone:
1) Provides documentation
2) The model provides for troubleshooting
3) It is a great way to train the next persion who gets to take care of it.
Best Regards,
Bob A.
FAGARCIA said:
it is Simatic 332-5HF00-0AB0 8-point 12 bit Analog output card. manual says 4-20 = 0-27648
I believe this card has 4 sided blocks on the side that have to be oriented correctly for voltage or current. Have you done that?
FAGARCIA said:
no.
I configure each channel to be 4-20 on the hw configuration only.
I would check for any type of configuration block or jumpers on the card. I can't recall for certain and don't have the manuals in front of me, but I do know that some of the Analog modules have either a bank of jumpers or a 'block' that has to be oriented correctly for current or voltage. There are also a different set of terminals to wire to whether you are sourcing current or voltage, so check your wiring too.
If your current is dropping it certainly sounds like either a wiring or hardware configuration problem.
Is the measurement with a 'load'?
Is terminal 6 connected to the ground?
Is the 24VDC connected to terminal 1 (+) and 20 (-)?
Are the grounds (terminal 6 for example) connected to terminal 20 (-)?
I've seen some funny measurements with the 4-20mA cards. Until we wired em exaclty how it is shown in the manual.
Edit: The analog output cards from Siemens don't have the 4 side blocks. It seems only the analog input cards have em.
logic as requested
Looking at the values I realize that I am not really sendind 27648.
that number is the shown on the screen but the display was in floating point, when changed to decimal is a much bigger number.
My problem now is not the output card but the logic to convert the real to decimal.
I enter 0-27648 directly into the PQW an I get the right 4-20ma
Here's some code that will work:
Code:
	 L	 DB165.DBD 144			 //0.0 - 100.0%
	 L	 2.764800e+002
	 *R								//0.0 - 27648.0
	 RND							 //0 - 27648
	 T	 PQW 262
As an alternative you could use FC106 (Unscale) from the Siemens library.
Dear All, I want to use a 4-20mA output from Omron AO module, so I did the following configuration: PLC used CJ1M-CPU22, rack 00 CJ1W-AD041, rack...
5,011
Good Day, I have a GE FANUC 90-30 plc with CimPlicity software. I wish to precisely control a current output (to provide to a remote solenoid...
3,186
We have a Rockwell 1734 IE8C 8 channel analog input card, but we don't know if this is sourcing or sinking. The user manual doesn't seem to have...
1,151
Good evening, just a dump question, I’ve configured channel no 13 with scalling as attached, then shown not linear reading, even when i simulate...
1,716
Good Evening , I have a 1756-IF16 Analog Input card already installed in a working ControlLogix Rack. I need to add another Analog 4-20 ma...
2,195