Iam using A&B (slc500) and/or TSX (micro/premium) and need to send sms when an alarm is triggered.
1. Can it be done directly from I/O (i.e I1.0 -> can memory bit, done with programming, surely). But without any PC/SCADA/HMI/OPC/etc. Kinda "hardwired" way..???
2. If HMI/SCADA is in use???
Thanks in advance...heil PLC :)
You can quite easily send SMS messages directly from the PLC.
Connect a GSM modem to CH0 of the SLC (i'm assuming you're using a 5/03 or higher) - use the AWT command within Logix500 to send the necessary AT commands to the modem as ascii characters (i.e. AT+CMGS etc) via STRING registers.
If you search the forum, you'll find sample code (i've posted a bit myself...)
Hope this helps! (y)