AB 1746-NR8 Failure Issue
ChrisLG
Apr 2019
California
Thanks in advance for any ideas or suggestions.
Over the past 2 years, our plant has experienced the unusual failure of 3 separate 1746-NR8 modules installed in 2 different AB SLC503 PLC chassis. When the 1746-NR8 board fails, it appears to develop an internal short circuit. As a result, the board is pulling too much DC current and the internal protection on the power supply (1746-P4 in one case and 1746-P2 in the other) trips cutting power to the entire PLC chassis. The high current issue continues to exist if the module is disconnected from its associated RTDs. If the 1746-NR8 module is removed from the chassis, the power supply internal protection will reset (after an off/on power cycle) and provide power normally to the PLC chassis.
In several years of working with our SLC503 systems, I have only experienced this issue with 1746-NR8 modules. I have had other modules fail but never in a manner which causes the internal current protection in the power supply to trip.
There are no obvious signs of a short circuit on the 1746-NR8 module.
Has anyone else experienced this type of 1746-NR8 module failure? If so, has anyone been able to identify the cause of the high DC current load from the 1746-NR8 module?
I had three 1746-NR8 card go bad in 3 separate controllers. Anyone know of a defect or recall? Getting a bit scared I may need to replace all my...
2,750
I'm new at working with RIO and have a question I was hoping somebody could please help with. I've got a SLC 5/05 with a 1747 SN Remote IO...
3,088
I have a question about config this Input Module. I'm using a SLC 5/05 and trying to config inputs 5-8. Inputs 0-4 have been done. In the advanced...
2,603
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
184
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
1,029