We have an AB 3000i using DeviceNet. It has been working fine for over 5 years. About a year ago we got an E01(Non-Volatile Memory) error. Power cycling the unit a few times seemed to fix it even though it says its a unrecoverable error. The last few months we have been getting E11 (Illegal Hall State) and E19 (Excess Position Error) codes. They are very sporadic. We can go 3 or 4 days and not get any codes then get 3 or 4 in one day. Mostly E11. A few times the E11 has popped up even with it sitting idle. Sometimes the codes can be cleared with a Reset. Sometimes it takes a power cycle. First thought was replace the Servo, so we did. Did not help. The cable is in a fixed path and does not move. I have checked it over well and it looks fine so I can't see it being a cable problem. It is grounded as it should be. So thinking next step is to replace the Drive.
I have a new 3000 drive to try and the Ultraware software is on the equipment. Is my thinking correct in that I can use the Ultraware software to export the old drives parameters, replace the drive with the new one and then import the parameters to the new drive ? Any other suggestions ?