AB AENT - Communication Issue
Jun 2017
Coimbatore- Tamil Nadu
Hi... Good evening all...
In AB 1794-AENT module and AB 1734-AENT Module suddenly below problem has come
AB 1794-AENT module - Network status solid red blinking has come instead of green colour .
AB 1734- AENT Module- Pointbus status solid red blinking has come instead of green colour.
In Field side, all equipments are not running but in SCADA it was showing healthy condition ( Running Status ). AB 1794-AENT located at Main PLC panel and AB 1734- AENT located at MCC panel.
After seeing this condition, I did power recycling at both zones then automatically some of DO relay are energized and Main Network switch ( Pro Curve - HP Make ) status i checked and System come back to normal after power recycling.
Can anybody tell me exact problem what actually happened and due which its happened.
Manuals for your two devices, which have tables to interpret the status indicators:
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1794-in082_-en-p.pdf
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1734-um011_-en-p.pdf
On the 1794-AENT, a blinking LED means "One or more of the connections in which the adapter is the target has timed out."
On the 1734-AENT, a blinking red LED can mean a few things (see manual), but the most likely cause, given that it was working previously and that the 1794-AENT also had the symptoms above, is "Node fault (I/O connection timeout) occurred."
Nobody can be sure of the "exact problem", but it's likely that there was a communication failure between each of these modules and the associated controller, and that cycling the power caused whatever was causing the root issue to re-initialize correctly.
I have a network with 17 1734-AENTs. One AENT losses communication regularly. The symptoms are AENT Module Status - Green Network Activity -...
4,508
I have an issue with this 1734-aent, This has been an existing set-up. The 1734-AENT 192.168.1.2 card has been configured through Bootp with the...
16,839
Hi to All, Actually today i had tried with this concept,but no result.. i have L32E cpu and 1734AENT with IB8 and OB8(in the testing kit) please...
2,557
Hi, I am working with project where i need to only monitor Analog Inputs, there is no control with that AI. I would like to know whether 1794 AENT...
4,706
Dear All I am working with a compact logix system and 1734-AENT for a remote IO. I can view the PLC program online via Ethernet / IP driver of...
16,159