I am using ab 1769-l30er for redundancy logic, the secondary controller is not being recognized, the icon is replaced by a yellow question mark, its showing error msg as "failed to create module profile , module profile or eds file not installed". I have uploaded eds file from linx, and aop's is available only for aentr modules on ab site.
# i have attached the screen shot.

dak psi err..jpg
 
Using hot back up tool it can be done , it's working as of now ,, I am facing d problem bcos the logic was developed and hot backup created in other lap top. I'm using d same file in an another laptop , while d error is generated.
 
CompactLogix shouldn't be used for redundancy. It's not designed for it, and the technotes that describe the "soft backup" are filled with disclaimers and warnings. Rockwell does not distribute the "Logix Hot Backup Code Generator" directly to customers, and advises customers who are trying to use these techniques that they can only obtain assistance from their local sales office, and will not distribute it to the local sales office without a commitment to engage a local commercial engineer. It is Rockwell Automation's express desire and intent that anyone using these techniques work closely with their local sales and support office.

The insertion of another CompactLogix 5370 series controller in the I/O tree is no different for "software redundancy" than it is for ordinary Produced/Consumed tag exchange.

I think the problem in this case is that jagadeesh17js is attempting to upload the project directly from the controller without having the source project on his PC, which requires that all the modules be created by Studio 5000 Logix Designer.

I recommend that instead he copies the project file (*.ACD) from the computer on which it was developed to his computer. He can open the project offline, then upload any changes that are in the controller.
 

Similar Topics

Been seeing a high failure rate on these PLC's on 2 of our process. The control power is feed through a APC UPS to a 24VDC power supply to power...
Replies
14
Views
4,038
Hello. I am trying to figure out how to setup a PID in Control Logix 1769 Controller in a way that it would control a drive speed by sending...
Replies
3
Views
1,624
Hello guys, I need to add in a few discrete and analog cards for an existing 1769 Compact Logix system at a local Treatment Plant for an...
Replies
9
Views
3,697
Hello Everyone, First of all, I would like to thank you for everyone who helped me in the previous post and this platform is really helpful for...
Replies
2
Views
3,190
Hello Got a red solid OK light and I can't get connect to the controller. Any help!
Replies
2
Views
2,175
Back
Top Bottom