AB PLC 4-20mA no response from PLC
A test would be to wire a precision 500 ohm resistor (at least 1/2 watt) from the VOLTAGE input to common then wire the current signal also to that voltage input. The voltage drop across the 500 ohm resistor at 20 ma would provide 10 volts. (The 250 ohm resistor suggested by Balash would yield up to 5 vdc at the 20 ma point.)
Actually, disconnect from the input module and just wire the resistor from the analog output of the device to the 24 volt supply common then measure across it with varying temperatures. You should see a low to high voltage (max 10 volts) with higher temperatures. If this works out then attach the setup to the voltage input on the PLC.
Regarding possible damage, the PDF for the similar stand-alone card notes that possibility, especially if a voltage input was applied to the current terminal.
Thanks to both of you! I'm currently doing a project as a student and got this PLC second hand. I never had to use the analog current inputs until recently, hence the reason I've been so confused. I'll resort back to the voltage inputs and that should be enough to get me through! I can't express how grateful I am and if I have any issues or even some luck I'll try and find time to come back and let you know my results! :)
Hi, I am just exploring the options to replace an outdated filling valve controller for a can filler. It has 78 filling valves and runs at max...
4,536
I'm using micro 820 2080-lc20-QBB Plc that have only one analog out 0 to 10v. I want to connect one mov that is working on 4 to 20ma. How to...
2,233
Hi; I have installed a temperature and humidity sensor Autonics THD-R-C which gives 4-20mA signal out. The signal is connected with Fatek...
2,763
Help me ! noise signal plc ? How to prevent noise for plc?
1,885
Hi, I'm a noob after some help if possible. I have been using a Click PLC with a 0-20mA analog input module, quite happily, for some time now. I...
1,814