AB PLC5 communication
sk1984
Feb 2017
Ranchi
I am trying to establish communication between two Allen Bradley PLC5 plcs on dh+ port(which is a three pin connector).Both of them are having node address 1.Please tell me the steps how to configure both plcs to communicate with each other.what are local and remote messaging?Is it necessary to know about them in this context?Is any software change required?kindly help
Welcome to the Forum !
What is the exact model number of each PLC-5, and which Port number is the DH+ port ?
Most PLC-5 controllers have "Channel 1A" configured by default for DH+ protocol, and Channel 1A's address is set by DIP switches on the controller. You can read about how to set those up in the PLC-5 user manual.
In general, controller-to-controller messaging is considered "Local" DH+ messaging. "Remote" messaging is much more complex and involves multiple DH+ networks that are carefully connected with network bridges.
You can read about DH+ messaging using the MSG instruction in the PLC-5 Instruction Set Reference.
Links to useful documents:
PLC-5 Enhanced and Ethernet Hardware User Manual
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1785-um012_-ru-p.pdf
http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1785-rm001_-en-p.pdf
Thanks for replying.The model is PLC5 40C .The DH+ port is 1A.Also connections are made in 1B(remote I/O scanner).Will changing of DH+ address also effect devices in 1B.Will devices connected in 1B loose communication after changing DH+ address?Is any ladder logic like DH messaging need to be incorporated for message exchange?Any changes in processor properties?
No, as Ken stated channel 1A's DH+ address is set by dip switches on the processor. It has no effect on channel 1B.
No
Yes, a message instruction will do this. See the manuals provided by Ken above.
How much data do you want to exchange?
No-one has mentioned that your two PLCs must have different node addresses...
Dear Expert, Currently I am working in old PLC5 to get the data from Weighing scale delivered by Mettler-Toledo. Here is the result so far: 1...
1,128
I've been searching the forums for hours and I've found many things to try but just haven't found the right answer yet. I have a running PLC 5...
1,868
In one of my project, end-user wants to connect Controllogix 1756 IO's with PLC 5/40E controller on DH+ protocol. 1756 DHRIO card is installed in...
6,738
Hello Friends I need to share some bits between a PLC 5/30 and a 5/04 CPU through DH+.* Is it possible? How can I do that? With MSG...
1,871
Hello, I have a PLC5/30 unit that controls an existing machine. I need to communicate to it from Iconics Gen64 SCADA software. I was told that...
1,406