AB Power up handler routine
dginbuffalo
Dec 2010
Buffalo,NY
630
Hello. i have an AB Compactlogix with 2 racks of remote ethernet I/O at a station that suffers from occasional power outages. when the power comes back up, the PLC faults occurs because at least one required connection is not established before going to Run mode. This is a 3/23 type fault code.Can i just put some kind of delay timer in the power up routine and then go run mode? I know one of the remote racks just isn't ready normally annd as soon as i clear the fault, it's good to go again. unfortunately-it's an unmanned site in another state :(
Find out which module is the culprit and then, within the RSL5K Online application file, open up the respective module's configuration applet and under the Connection tab un-check the "Major Fault On Controller If Connection Fails While in Run Mode".
Well...You really don't want to fault a CPU if all of a sudden any I/O and/or connections are missing...I very seldom check the "Major Fault On Controller If...." option.
Our approach to this kind of situations is based on programming logic which is monitoring the status of the critical modules and, in case of communications failure, trigger some sort of "emergency shut-down" routine.
Chapter 1 Pg.14-15 of http://literature.rockwellautomation.com/idc/groups/literature/documents/pm/1756-pm015_-en-p.pdf
will give you an ideea of how to monitor any connection's status.
the slc500 plc's has a fault override at power up bit in the ststus word that you can set for speciality modules like etherner comms modules.
you might look into the logix family for something similar.
regards,
james
Do i have to monitor the status of all modules in the remote rack also? i'm wondering if i monitor just the remote ethernet adapter, if that would show a fault when one of it's modules fault? regardless- if i uncheck "major fault" i guess i will have to have a fault handling routine to reset try to reset the faults after power is restored to the station.
Hello, I'm new here and new to AB programming. I come from the land of DeltaV :) I have a CompactLogix 1769-L1, and found out how to...
1,410
I have a controller issue I think. 1756-L63 Using RSL5000 v20.05 I can verify a project and download it, do online edits and monitor fine...
2,789
Hey folks. I created a routine in the power up handler folder in the controller in a 1769-L30ER. I wanted to have the controller go through a...
8,363
Hello all, thanks for taking time to read this. I'm having an issue with testing the power-up handler and I cannot get a fault to occur. In the...
3,391
Hello all, I am currently trying to program a PowerFlex 525, version 7.0. We had a power outage recently and when the power was restored, the...
234