ControlLogix Power-Up Handler
Karlore
Mar 2016
In a house
Hello all, thanks for taking time to read this. I'm having an issue with testing the power-up handler and I cannot get a fault to occur. In the power-up program, I have configured a main task and a fault task. In the main task I have a single rung which JSR's to the fault task with a code of 999. I expect that when I download then place the PLC in run, that this should trigger a fault, but it doesn't. Another piece of information is that I'm running the PLC in RSEmulate. Is there something else I'm missing?
When the controller detects a fault, the control jumps to the fault routine. I think that jumping directly with a JSR to the fault won't trigger any fault: it's just like jumping to any routine.
If you want to generate a fault, just try doing an out-of-index operation on the main routine.
According to Rockwell's Manual on P. 28, this is exactly how you're supposed to test faults.
Edit: I just noticed that this will only simulate the routine and not generate an error (P.27) but the wording below it is misleading. Does anyone know if this will actually trigger a fault?
Time for me to ask a stupid question: is your rung unconditional or is it set up exactly like the manual shows? If it's just like the manual, did you toggle Tag_1.0?
Another stupid thought: check the spelling of your fault task in your JSR to ensure it matches the actual name of the task.
The Power Up Handler is a specialized task. It is used to run logic whenever the controller powers up. It does not execute on a transition from Program to Run which is what is happening when you are downloading. I don't know that the emulator can simulate a power cycle.
And your terminology may be confusing things too.
  • A Routine is found in a program and contains logic
  • A Program is found in a task and is used to store and organize routines
  • A Task organizes the programs and determines what runs when
I think you are saying "task" when you mean "routine". The JSR means Jump to SubRoutine.
OG
No problem, yes, similar to the manual with a single bit to JSR to the FaultRoutine. The rungs are powered.
Hi: For ControlLogix. Is there a way to "trap" when processor is powering down? This mean leave a bit latched or a value written to a tag? Is...
247
Im trying to make my own DIY ControlLogix power supply and have had some success, but not every module powers up. I am using 4 seperate power...
934
Hey everyone, I've tried the search function for similar issues but couldn't find any relevant info. Issue: I have a Controllogix 1756-L72/A...
1,621
I am trying to add three AB 1426-M6E Power Monitor 5000s to the Device Tree of my Control logix application. Processor is L62 v. 20.12 Logix5000...
1,738
Had an issue at a plant this morning with comm's loss on equipment. Found a ControlLogix rack not powered up. Before I got meter to see if I had...
1,565