You should ALWAYS have reactors or some other form of impedance protection ahead of drives, especially small drives. You need to slow down the rise time of ringing transients that can affect the DC bus, but are too fast to be captured by regular hand held meters. These transients can be caused by other large loads being switched on and off in your facility, even a neighboring facility or even grid switching transients from the utility themselves (which they will deny, deny, deny they exist, until you present them with evidence on paper).

The quick-and-dirty rule of thumb is that if your supply transformer is more than 10x the kVA of a VFD, you need to put an input impedance component ahead of the drive. It could be one reactor for one drive, or one reactor for 10 drives (properly sized), it's all the same. This is what DickDV had alluded to back in 2011 when this zombie thread was still alive, in his suggestion to the OP to add a drive isolation transformer. That may be a more extreme version of the same principal, because it too adds impedance. It also adds more protection against common mode noise coming in from other systems on the same bus, but that is rarely a problem with modern VFDs now. I only use drive isolation transformers when there is a Delta power source or a resistance grounded Wye that might be dangerous for the VFD. Otherwise, I just use reactors, they are cheaper and smaller. Either way though, you need to do something.
 

Similar Topics

All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
88
So our Powerflex 525's are set up to allow REMOTE operation from PLC through network. But if network is lost we want to be able to run in LOCAL...
Replies
5
Views
583
Hello, guys I am having an issue with Pflex 755, when it is stopping the motor, it is going on fault 9 " Transistor Over Temp". Has anyone dealt...
Replies
1
Views
491
I recognize that I need to factory reset the drive and that P053 is my ticket. Problem statement: I can't get passed the fault display to get to...
Replies
5
Views
1,517
Hello. We use AB PowerFlex 7000 drives in a pump station. The operator just called to report a fault on one drive: "STATUS: Faulted" "FAULT: DI...
Replies
1
Views
665
Back
Top Bottom