Can anyone please advise me about the least expensive and most logical way to interface (3)-Allen Bradley PowerFlex 40, (1)-400 and (1)-70 drives to my SLC 5/03 PLC DH485 network?
The 3 ABPF40 drives are about 1200' away and the other two within 30'.
Thanks for any assistance you might have.
Protocol vs. Signalling, Round 42
You won't get the drives directly onto the DH-485 network. Even though each drive has an interface option that includes an RS-485 electrical interface, none of them support the DH-485 network protocol.
If it were my system, I'd spring for a Prosoft MVI46-MCM module and equip the PowerFlex 70 with an RS-485 Modbus RTU protocol interface (20-COMM-H). The PowerFlex 40 and 400 already support Modbus RTU natively through their "DSI" serial port.
Use one MVI46-MCM port to connect to the three far-away drives and the other to connect to the nearby ones. Configure both ports as Modbus RTU Masters, define the polled registers in the Master Transactions table, and you're in business.
If time and trouble are valuable to you, then the Prosoft card will save you more than enough of both to justify the hardware purchase.
Thanks for your reply Ken. I was wondering if using the ProSoft RTU-5/03 might be an option? Would I be able to parallel or slave my Flex 40 drives? I have a PV600 DH485 terminal to connect also. What would I use for my online programming port?
The Prosoft RTU-5/03 implements only Modbus RTU Slave on the Channel 0 serial port of the controller. You need a Modbus RTU Master port.
You can connect your DH485-protocol PanelView (it's always best to post the part number) to the Channel 1 DH485 network port of the SLC-5/03.
Use the Channel 0 serial port of the SLC-5/03 in DF1 Full Duplex mode to perform upload/download/monitoring/editing of the SLC program.
Install a Prosoft MVI46-MCM module as described above to act as a Modbus RTU Master to the PowerFlex drives.
Hi, I have a PFlex 400 networked with Dnet over 22-COMM-D as well as a 22-HIM-A3 on panel front. I am using the drive from remote as PID...
2,742
I've read a bunch of the post on here as far as communicating between the ML1400 Channel 0 and the Powerflex 400 via RS485. I cannot for the life...
1,869
Hello I want to set up a communication through GSM or LTE from a PowerFlex drive and other instruments (flowmeter, level meter, etc.) to PC 100...
894
Hi!, I have 4 powerflex 400 recently installed and my customer is asking me if I can set the drive up to rearm automatically after a power fail. I...
1,616
Hi, I have this configuration and I´m receiving 203 (timed out) error from the I/O tree in RSL5000. Although, I can read parameters from the...
1,465