Hi, I'm facing problem with AB GuardMaster Safety Relay (MSR-125HP 440R-D23171).
I'm working on a project that has Safety Catagory-3 Door Lock switches and Emergency stop switches. If any safety issue occurred i.e. if any one of the switches is activated then the CH-1 & CH-2 output of the Safety Relay (13-14, 23-24) will be disconnected. After closing the safety issue and after manual Reset the safety relay returned to its normal condition.
As per the datasheet I have connected the relay with my safety circuit. But CH-1 & CH-2 are not latched.
This is not a normal safety unit it is a two button operator interlock are you sure you have the right unit for the application.
I won't give you a yes or no answer, but...
Have a look at the AB literature, they have good wiring examples for this.
Search Publication 440R-UM013E-EN-P – March 2017 to find
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/440r-um013_-en-p.pdf
Search Rockwell Automation Publication SAFETY-WD001L-EN-P - March 2020
https://literature.rockwellautomation.com/idc/groups/literature/documents/wd/safety-wd001_-en-p.pdf
You will find the relay part number you suggested (440R-S12R2) in there.
Good Evening , I tried 2 other MSR 127TP Safety relays , and both do not have voltage coming our of S21 . What could case that ? I have the...
1,455
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
115
I have an application where I want to use a safety relay in combination with a flame detector as the sensing element. The flame detector has relay...
23
1,094
I want to improve a semi custom product I am delivering to a customer with implementation of safety relays. The system is fairly simple with just...
593