Hi, New guy here.
We have older Allen Bradley SLC 150s in our six Automated mini-load supply units. One unit tripped a CPU fault, and will not reset. We have tried known good units from supply and from other mini-loads. PLC does the exact same thing and then is fine when reinstalled in the other machine. All 115AC and 24VDC power inputs and sensor input/output values are correct. Double checked all wiring and encoders. Tried swapping out the Eprom, no dice. We hooked up the pocket programmer to try to clear and put it back in PC run, but the programmer will not communicate, Error 10. Has anyone ever seen a situation like this? I'm thinking it must have a hard short somewhere, but we've disconnected everything on the input side. :confused:
Thanks in advance....
Have you tried removing all inputs and seeing if it would reset?
Normally the fault would not be because of an I/O I would think a value in the CPU, program error or loss of program.... BUT maybe the encoder input
When you changed the CPU did you try the other one in the other machine?
Have you tried to bench test the faulted PLC? By that I mean just connect the power only from an isolated power supply to the plc and the programmer to see if there is something on the machine causing the problem. Also, I'm guessing that you tested the programmer on a known good PLC to verify that it can communicate.
How can I get a schematic for it? I am unable to communicate to it using PCIS with a 486 PC and suspect the SLC150 to be faulty (found in a junk...
3,115
HELP! I've been searching & searching for the software to run my SLC150 PLC for DOS 6.22 and for some reason, every link I have found for it -...
1,155
Hi, I have an old SLC 150 processor that is throwing up a CPU Fault light. I have an EEprom program chip for it, but I can't get it to load up...
2,342
We have 3 SLC-150s that we are using, we would like to create a print for them and diagram the program so when we get approval we can replace them...
2,656
Hello, I am completely new to PLC's (and forums) and have been tasked to repair/upgrade a conveyor system at my college. It currently has an Allen...
2,696