ABB ACQ810 VSD Start Enable

Join Date
Nov 2016
Location
Kinross
Posts
7
Hello All,

Not exactly a PLC question but more looking for advice on a PROFIBUS controlled ABB ACQ810 VSD.

The drive is controlled over the fieldbus network and the command word is all correct and the speed reference can be seen at the Drive when in remote but the drive will not start. No voltage out to the drive or current feedback at all.

The activity arrow has a dotted line which indicates that it is not receiving the run enable.

The parameter for the run enable is 10.11 and it is pointing to an address which is A.430.000, Does anyone know what this parameter is actually pointing to as I cant find A.430.00 in any of the manuals. I thought perhaps it is a active programming adress but I have no real idea.

The drive will also not start in local mode either direct from the control panel so I think the comms network is fine.

Any help would be much appreciated.

Thank You
 

Similar Topics

Hello All, Not exactly a PLC question but more looking for advice on a PROFIBUS controlled ABB ACQ810 VSD. The drive is controlled over the...
Replies
1
Views
1,036
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
Replies
2
Views
90
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
147
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
Replies
4
Views
211
Hello all, I have an ABB PLC (PM573) and it has without MC card. I need to take backup from PLC to PC (in automation builder v2.7 ). My...
Replies
10
Views
448
Back
Top Bottom