Abb acs550 earth fault even when not in run.
g.mccormick
Jul 2012
IN
961
Hey all. I tried to startup a drive last thing before leaving for the weekend. On power up, the drive constantly gies earth fault. This is with the drive in stop mode, not even trying to go into run yet. This was a used drive we had on the shelf. Im sorta guessing this is bad.
I opened the downstream disconnect and it still did. I will disconnect leads entirely on monday
I've also seen bad current transducers do similar, stupid things. The ground current is sometimes calculated by the difference between the 3 outputs. Something like. 'If it the current went through there and there, but not there, then it must have gone to ground'.
Luckily, a 5hp drive costs less than a good dinner-date these days!
Well I disconnected the load leads at the drive this morning and powered up, the fault was gone. Luckily!
We found a pinched/grounded wire about 1foot from the drive in a LB cover.
Wire fixed, drive and pump running.
Thanks for the help all.
I just replaced this drive as the old one went out when the plant had a power surge/flicker. 1-Installed the drive 2-Powered up 3- Got an...
1,651
Hi Team, I am working on one Paper Coating machine, My Winder, infeed, Coater and Unwinder is runnning through ABB's ACS550 VFD, My winder is...
1,313
Iam getting Fault F021 ("System Fault Current Measurement is out of range"),Any help ??
3,007
Please i need help i lost all setup parameters to control 3 pumps pressure i put again some of them but i get stuck in ref 1,2 choice and...
1,442
I am having problems connecting my L32E to an ABB ACS550 RETA-01 Ethernet/IP Module. AB tells me the problem is with the RETA and ABB tells me it...
2,385