ABB ACS600 running at Constant
kobena
Dec 2005
Takoradi
I have an ACS 600 drive for motor control. The drive receives a 4-20mA input from a PLC at terminal AI2. The 4-20mA signal changes but the Motor runs at constant maximum speed displaying AI2[mA]=20.3mA.
Could someone explain to me why the drive is ignoring the mA input from the PLC? Can 21.1 which is set to DC MAGN be a factor?
NB: I have set 11.3=AI2;Min AI2=4mA;Maximum AI2=20mA
Clearly, the VFD thinks it is getting max mA signal, so it is naturally going to run at max speed. Have you checked the mA signal at the VFD input terminal? It appears that your analgo output isn't doing what you think it is. Are you sure the VFD is set up to track AI2 and not AI1?
Thanks Tom for the reply. I have really tested the VFD at the input terminal. I even simulated the signal at the VFD terminal with a multimeter from 4mA to 16mA at intervals of 2mA and was still getting the maximum mA signal. I have setup to track AI2.
Can any1 help me with how to access & change parameter group 10 of ABB ACS600 drive Presently the drive is communication with AC80 PLC on FO but...
2,766
Hi Everyone, I would like to know how to test the communication module of an ABB drive ACS600. Set point to the drive is being given via a...
3,048
I have a customer that just purchased a used paper slitter/rewinder. The original owner did the initial teardown and shipped the machine to my...
4,820
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
90
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
147