ABB ATS Communication & IF statements vs CASE
Sham
Sep 2019
Australia
152
Hi all,
I am facing issues with communication to the TruOne ATS of ABB via plc. Plc is M251 of SE. Majorly 2 issues:
1- writing to the modbus register via plc is not not reliable. Like, we can write the values once or twice, but after couple of instances, the ATS doesn’t action on the command we send. Surprisingly, it does read them. The reason why I m sure it reads them is that on the parameters section, it shows those settings. For example, if I want the preferred source to change from S1 to S2, it will be shown on the ATS screen, but it won’t just switch after switching a couple of times. But if I send commands via modpoll, it is smooth and switches as many times as we ask it to. But once it goes in that glitchy mode of not responding (after we send commands via plc), it won’t even respond to the commands from modpoll.
2- case statements vs IF statements.
For the same program, i tried writing values to thr register using if condition, and even though the logic was fine, values were just not being written (I could see the commands being sent, but not getting written in to the ATS register at all). But when I tried same with case statements, it worked.
Any help will be greatly appreciated.
Thanks Kal. But why is it then working fine with modpoll? And if statements are not writing anything, while case statements do. I will review thoroughly the code today again surely
You are probably using multiple IF statements instead of ELSIF.
In such case (hah!) the last IF statement will be triggered in the same scan cycle regardless of the other statements being true.
I guess that is correct, but the main issue was spotted in the code that was writing the values to the registers. All good now!
I dont understand the reason though...why will the last IF be true is conditions are not met? You mean all the IF statements can be triggered in the same cycle if conditions are met?
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
116
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
168
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
226
Hello all, I have an ABB PLC (PM573) and it has without MC card. I need to take backup from PLC to PC (in automation builder v2.7 ). My...
473
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
200