Hi, Wondering if anyone knows how to test a magflow unit.
The flowmeter is the 2 part unit. Not sure if it is the pipe section or the display section that is faulty.
I am not worried about calibration, just want to determine which piece needs replacing.
Regards Alan Case
Alan,
Normaly ABB instruments support the Hart protocol. If you have a handheld hartcommunicator your problrm is solved in a minut?
If your not sure which one to replace, replace the elektronic part. You can't anything wrong be dooing this.
Rudi
I have to agree with Fritz, in most cases it's the transmitter that goes bad and not the flow tube. However, if you are measuring a fluid that can coat the electrodes in the flow tube, such as glue or paint, then sometimes the electrodes will become coated with material and require cleaning. Most devices that support the HART protocol have built in diagnostics and can tell you what's wrong with themselves.
Ken
If it's a MagMaster, you can talk to it with a serial link using hyperterminal or similar. I think the default setting is 2400-8-N-1. Default passwords are 'user' for level 1 and 'engineer' for level 2.
ABB Magmaster series magnetic flow meters can be checked with the help of CALMASTER simulation tools. If you do not have the CALMASTER, call the ABB's Service Team. By calling 1-800-HELP﷓365, the customer can have an ABB certified CalMaster technician scheduled to perform a validation on site.
Sunith
Most of the problems with these types of unit are the cables, check the cables and screening are OK and as per the installation instructions. You will get a fault if the 3-core signal cable does not have a balanced impedance i.e. if one wire is high resistance.
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
114
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
163
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
225
Hello all, I have an ABB PLC (PM573) and it has without MC card. I need to take backup from PLC to PC (in automation builder v2.7 ). My...
472
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
197