ABB Sami - Star frequency converter
esl
Apr 2002
surat
Is there anyone using ABB samistar frequency converter, I need help regarding GTO failures.
Its a scalar drive of 1250 kw capacity having multiple inverter conifiguration( Master - Slave).
I have had experience for a number of years with Sami drives up to 800kw which from memory are similar to the larger drives. i notice your question was posted a long time ago and may well have been resolved then. If not i offer the following comments relating to GTO failures. It is most important to torque the replacement GTO's as per the information provided by ABB. Failure to do this will result in sporadic failure of the GTO's. Use of calibrated torque meters is the way to avoid this. If you have done this and have further details of your problems still requiring a solution please e-mail me your question.
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
90
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
147
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
211
Hello all, I have an ABB PLC (PM573) and it has without MC card. I need to take backup from PLC to PC (in automation builder v2.7 ). My...
448
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
185