ACS550 ABB drive
faehigkeit1
Jul 2007
virginia
77
Hello,
I know this isn't a plc question but thought I would see if anyone has experience with this application.
I have available 0...10vdc for pid error corection.
I want 5vdc to = no correction
below 5vdc to correct positive
above 5vdc to correct negative
Just wondering if anyone has done this using ABB ACS550 drives.
Thanks for your time.
Dean
Not really clear on what you mean. Is the 5vdc signal going to be the setpoint or is it somehow part of the process signal coming back to the drive?
I have a 0..10vdc ref signal to analog input1
I have a 0..10vdc signal to analog input2 for error correction coming from a dancer assy. When the dancer is in the middle of its travel position (5vdc) no error correction needed. Above and below 5vdc as the dancer swings out of position would be the error signal. I am in contact with ABB tech. support but am still struggling. I have no experience with pid loops.
Thanks for having a look though
Dean
OK, let's see if I've got this. You've got a 0-10vdc signal on AI1 for a setpoint and your dancer signal also is 0-10vdc and is coming into AI2. You desire that the dancer operate in the middle of its range which is 5vdc on its feedback signal.
First, be sure you set the little yellow switches for voltage input rather than current input. These are located just above the control terminal strip and the factory default is voltage for AI1 and current for AI2. You need to change the second one to voltage. Also, you need to select PID Control macro in Parameter 99.02 and Vector-Speed in 99.04.
Before you attempt to set up the PID control, you need to run the drive and motor as a simple speed regulator and tune the speed loop in Group 23. Typical gains will be 30 in 23.01 and .5sec in 23.02. Usually 23.03 is left at 0.0.
Then you can switch to PID control and tune the outer loop in Group 40, Parameters 40.01, 40.02, and 40.03.
If you want the dancer to operate from the middle of its range then the setpoint input needs to be set at 5vdc. This sets up the neutral position for determining error.
Your mention of a dancer makes me think you might be doing a winder or unwinder with this drive and motor. If you do not have direct experience with tension control and winders, I strongly recommend that you hire someone to do this for you. They are one of the toughest applications to do correctly and your chances of getting it right are near zero. In fact, my chances are no better---I always defer winders to a system integrator that specializes in web process control.
Good luck.
Hello! In the attached photo you will see my ABB Drive in my device configuration tool in TIA v12. It will be controlled by PROFIBUS. I think...
2,313
Hai Folks Have anybody got experienced with ABB ACS550 Drive... I have an Application of Speed Control of AC Motor... I'm gonna use ABB...
22
15,101
Hi all First project on a GE 9030 and would like some help with setting up comms to an ABB ACS550 drive. Scenario: 10-slot rack with CPU363...
4,943
I just replaced this drive as the old one went out when the plant had a power surge/flicker. 1-Installed the drive 2-Powered up 3- Got an...
1,651
Hi Team, I am working on one Paper Coating machine, My Winder, infeed, Coater and Unwinder is runnning through ABB's ACS550 VFD, My winder is...