ACS550 and M580 PLC INVERT SPEED REF. ERROR

cedric.turmel

Member
Join Date
Jul 2019
Location
Québec
Posts
2
Hi,
Has anyone had this problem:
- I send a speed reference to my ABB ACS550 Drive via Modbus TCP to it's register via an INT. However when I have to transfer a modified project to the PLC sometimes I have to invert the BYTES of the INT for the speed reference I send to the drive or else it receives the wrong reference and the drive gives DIR LOCK error 2004.

If I redo a project transfer to the PLC everything comes back to normal.
My quick fix was to add a bool to activate if needed to reverse the INT.

I would like top permenately fix this proble. Spoke with ABB and they never heard of this issue.

Any help?
 
Just to determine whats wrong, try to capture the communication using wireshark - when its woking and not to rule out the control system.
 

Similar Topics

Hi, I am using ACS550 for Winder in Winding Application. I want to run the Drive in Torque Control Mode. I have done following parameterization...
Replies
0
Views
1,163
I just replaced this drive as the old one went out when the plant had a power surge/flicker. 1-Installed the drive 2-Powered up 3- Got an...
Replies
4
Views
1,653
Hi I need help!im working onA ACs550 An I have 3wires from a start an stop button s we’re do I hook up these wires? I know it’s on page 79 but...
Replies
9
Views
1,958
Hi Team, I am working on one Paper Coating machine, My Winder, infeed, Coater and Unwinder is runnning through ABB's ACS550 VFD, My winder is...
Replies
0
Views
1,315
Hey all. I tried to startup a drive last thing before leaving for the weekend. On power up, the drive constantly gies earth fault. This is with...
Replies
8
Views
2,208
Back
Top Bottom