Adding RIO-MODULES for 1747-ASB in Logix 5000

jackhenkel

Member
Join Date
May 2012
Location
Grand Rapids
Posts
62
What I am doing is converting a logix 5 program to logix 5000. What I am stuck on has to do with the RIO rack. I am using a 1747-ASB that is setup as a 3/4 Rack (6 I/O) groups. I have 5 modules that need to go in. 1746-OA16, 1746-IA16, 1746-OA16, 1746-IA16 and 1746-NIO4V. I will be using single slot addressing. What I am confused on is the slot and group number.

For Example: I want the 1746-OA16 to be my first module at group 0, slot 1. 1746-IA16 to be group 1 slot 2. 1746-OA16 group 2 slot 3 etc...

I have read through the manuals but am not quite understanding?? Any help is appreciated. I will continue to try.
 
Are you using the 1756-DHRIO or the 1756-RIO scanner ?

I realize the nomenclature is confusing, but when using "One-Slot" addressing, the Group number correlates to the physical location of the module, while the "Slot" number is not used.

You will have

1746-OA16 Group 0
1746-IA16 Group 1
1746-OA16 Group 2
1746-IA16 Group 3
1746-NIO4V Group 4
 
On the left hand side you could see something like this in Logix 5000 controller Organizer:

[0:0] RIO-MODULE
[0:1] RIO-MODULE

What is the difference between the two in single slot addressing if the first number is the group and the second is the slot but you are saying slot number doesn't exist with single slot addressing correct?
 
It gets very confusing, but with traditional A-B addressing the "slot" number was only ever 0 or 1, defining the module placement in the left-hand slot of a group, or the right. The "slot" was never intended to be the slot in the chassis at all.

Be clear about the difference between Slot (capital S), and slot (lower-case). In the A-B world the former is an address, the latter is a location in the chassis.

They did themselves no favors when they advertised their chassis as 4, 8, 12, or 16 slot !!

When 16-bit I/O modules came out, most people used them, so used single-slot addressing. It muddied the waters between "Group" addressing, and "Slot" addressing, because in this mode "Group" = physical slot, and "Slot" = 0 always

Confusion multiplied with "2-slot addressing" to accomodate 32-bit IO modules, where a single physical slot (notice no upper-case here), can have two "group" addresses.
 

Similar Topics

I have never understood how the I/O is configured using RIO. In the tree there is only the RIO module, not the racks of I/O attached or all the...
Replies
2
Views
1,306
Hello all. I have a job to add a 1794-IE8 Card in slot 5 on an existing Flex IO Rack which uses a 1794-ASB communications module, which...
Replies
8
Views
3,012
I am having trouble adding an output modules to a remote io rack on a plc5 the processor is PLC5/80E it has 6 full RIO racks and 2 3/4 racks I am...
Replies
10
Views
2,923
I have this machine that is communicating via DH+ to a central Logix PLC. This PLC has two DHRIO modules and we are already getting data from this...
Replies
23
Views
3,982
I need to add a Flex Analog input module to a RIO rack (Rack No. 3) without shutting down the PLC-5 processor. Please suggest me how to add and...
Replies
0
Views
2,184
Back
Top Bottom