I've done this or similar with some graphics intelligence and PLC coding in a pure Rockwell environment (PanelView tocuhscreen and FTView SE SCADA). Maybe it's possible in your environment.
At each location a specific graphic screen is configured for setpoint manipulation. When the touchscreen graphic is opened, bits/bytes are sent from local PLC to remote to let SCADA know it's hands off - opening and/or manipulating its setpoint graphic is blocked. Any newly adjusted values are immediately sent from local PLC to remote (SCADA) PLC.
Vice-versa when the SCADA graphic is opened.
Force each setpoint manipulation graphic closed after a short period of inactivity and clear the 'hands off' bits. Ask/demand the users close the graphics when not using them as a standard operating procedure.
When neither setpoint manipulation graphic is opened you don't need to move any values back or forth. They'll have been updated during the last 'transaction'.